How to

How to


Products: Automation Server, AS-B, Enterprise Server, AS-P, Project Configuration Tool
Functionalities: Alarms
Product version: 1.9
5/7/2021

Configuring an Out of Reference Range Alarm

You configure the properties of a out of reference range alarm to meet the unique needs of your site.

Show More
action_close

​The out of reference range alarm monitors variable movements comparing to a reference variable. By setting an upper deviation limit and lower deviation limit, you configure the tolerance the monitored variable can vary from the reference variable before the alarm is triggered. The upper alarm limit of the monitored variable is equal to the reference point current value plus the upper deviation limit. The lower alarm limit of the monitored variable is equal to the reference point current value minus the lower deviation limit.

Note:
  • An out of range alarm with upper deviation limit, lower deviation limit, and deadband set to zero must meticulously follow the reference variable to not trigger the alarm.

 
action_zoom_plus_stroke Out of reference alarm triggers an alarm when the monitored variable goes outside the upper or lower deviation limit of the reference variable.

Out of reference alarm triggers an alarm when the monitored variable goes outside the upper or lower deviation limit of the reference variable.

For example, you have a reference variable that is designed to follow the optimal room temperature in a office. By connecting the reference variable and the variable from a thermistor, placed in the office, to an out of reference range alarm, you can set up the alarm to trigger when the temperature differs more than 5 °C (41°F) from the reference variable.

You can configure out of reference range alarms using shunt variable, time delay, and deadband. For more information, see Alarm Functions .

To configure an out of reference range alarm 
  1. In WorkStation, in the System Tree pane, select the out of reference range alarm you want to configure.

  2. On the File menu, click Properties .

  3. Edit the basic settings:

    Table: Basic Settings Page or Tab

    Property

    Description

    Type

    Displays the alarm type of the alarm.

    Name

    Displays the name of the alarm.

    Description

    Type to change the description of the alarm.

  4. Edit the alarm trigger properties:

    Table: Alarm Trigger Page or Tab

    Property

    Description

    Upper limit

    ​Enter the highest value the monitored variable can increase to before the alarm is triggered.

    Lower limit

    ​Enter the lowest value the monitored variable can decrease to before the alarm is triggered.

    Deadband

    ​Enter the range the monitored variable has to pass within the normal range before the alarm is reset.

    Monitored variable

    ​Enter the path to the variable that is monitored by the alarm.

    Reference variable

    ​Enter the reference variable that is compared with the monitored variable.

    Disable alarm

    Select to disable the alarm, for example, before deployment.

    Alarm state

    ​Displays the present state of the alarm. For more information, see Alarm States .

    Disabled cause

    Displays the cause for the alarm being disabled:

    • Shunt variable means that the alarm has been disabled by a shunt variable

    • User means that the alarm has been disabled by the user

    • System means that the alarm has been disabled by the system

    Alarm delay (s)

    ​Enter the time, in seconds, the alarm has to be within the alarm criteria before the alarm is triggered.

    Reset delay (s)

    ​Enter the time, in seconds, the alarm has to be within the reset criteria before the alarm state is changed from alarm to reset.

    Shunt variable 1

    ​Enter the shunt variable that is used to enable or disable the alarm. For more information, see Shunt Variables .

    Invert

    Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. For more information, see Shunt Variables .

    Operator

    Select AND or OR to add logic between the first and the second shunt variable. For more information, see Shunt Variables .

    Shunt variable 2

    ​Enter the second shunt variable that is used to enable or disable the alarm. For more information, see Shunt Variables .

    Invert

    Select to invert the shunt value, that is, enable the alarm when the shunt value is active and disable the alarm when the shunt value is inactive. For more information, see Shunt Variables .

  5. Edit the presentation properties:

    Table: Presentation Page or Tab

    Property

    Description

    Above upper limit message

    ​Type the message to display when the variable exceeds the upper limit of the alarm.

    Below lower limit message

    ​Type the message to display when the variable falls below the lower limit.

    Reset message

    ​Type the message to display when the alarm is reset.

    Category

    ​Enter the category the alarm belongs to.

    Prefix for alarm source name

    Type a prefix that is added to the beginning of the source name property of an alarm record.

    Above upper limit priority

    ​Enter the priority level of the alarm when the variable exceeds the upper limit.

    Below lower limit priority

    ​Enter the priority level of the alarm when the variable falls below the lower limit.

    Reset priority

    ​Enter the priority level of the alarm when it is reset.

    Same priority

    Select to set all priorities to the same value.

    Auto hide

    Select to automatically hide the alarm in the Alarms pane or Alarm View.

    Flashing alert

    Select to make the alarm row flash in the Alarms pane and Alarm Views when the alarm is triggered.

    Audible alert

    Select to make the alert audible when the alarm is triggered.

    Disable state-change logging

    Select to prevent an alarm state change from creating an event.

  6. Edit the user action properties:

    Table: User Action Page or Tab

    Property

    Description

    Acknowledgement type

    ​Select the type of acknowledgement for the alarm.

    Cause note group

    ​Enter the cause note group that is used by the alarm.

    Action note group

    ​Enter the action note group that is used by the alarm.

    Checklist

    ​Enter the checklist that belongs to the alarm.

    Required User Actions

    ​Select what actions the user has to perform when any of the listed events occur.

  7. Edit the attachment properties:

    Table: Attachment Page or Tab

    Property

    Description

     
    action_zoom_plus_stroke

    Add attachment 

    Click to add an attachment to the alarm. For more information, see Alarm Attachments .

     
    action_zoom_plus_stroke

    Remove attachment  

    Click to remove an attachment.

     
    action_zoom_plus_stroke

    Navigate to 

    Click to open the attachment that is selected in the attachment list.

    Display on alarm

    Select to display the attachment when the alarm is going from Normal to Alarm state. 

  8. Click OK .

  • Out of Reference Range Alarms
  • Alarm Functions
  • Alarm States
  • Shunt Variables
  • Priority
  • User Actions