Configuring the MS/TP Address

You must configure a unique MS/TP address for the RP and MP controllers that support MS/TP communications. You do so during installation by using position 1-7 on the address DIP switch.

Show More
action_close

You must configure the DIP switches as part of the commissioning process for RP and MP Controllers that support MS/TP communications.

For more information, see BACnet MS/TP Network Communications .

Tip:

Use only the 7 switches on the left. You do not need to use the switch on the farthest right.

See the table and graphic that follows for more information on the switches and their ON values.

Table: DIP Switch ON Values

Switch

ON value

1

1

2

2

3

4

4

8

5

16

6

32

7

64

 
action_zoom_plus_stroke Address DIP switches

Address DIP switches

For example, to configure address 6, configure DIP switches 2 and 3 to ON and switches 1, 4, 5, 6 and 7 to OFF.

For more information, see Configuring the MS/TP Address .

Configuring the MS/TP address
  1. In the RP or MP controller, locate the address DIP switch.

  2. Use position 1-7 to configure the address.

    Position 1-7 represent the binary values 1, 2, 4, 8, 16, 32, and 64.

    Tip:

    Position 8 is not valid.

  3. Activate the switch at the numbered position by moving the switch up and then deactivate it by moving the switch down.