earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: AS-B, AS-P
Functionalities: Hardware
Product version: 3.2, 3.3, 2022
10/15/2020

General Legrand Power Meter Properties

An important difference between the Legrand meters is that models 04677, 04680, and 04684 use transceivers with integrated failsafe receivers, whereas the model 14669 uses a transceiver with no integrated failsafe function.

Review of the RS-485 interface provided by the Legrand meters yields the following interface attributes:

Table: Interface Attributes of the Legrand Power Meters

Legrand Model

Transceiver

Transceiver Unit Load

Transceiver Failsafe

Meter Circuit Bias

Circuit Bias Load

Total Unit Load

Isolated RS-485 Bus

04677

Exar SP4082

0.125

Yes

10 kohm

1.200

1.325

Yes

04680

TI SN65HVD3082

0.125

Yes

10 kohm

1.200

1.325

Yes

04684

TI SN65HVD3082

0.125

Yes

10 kohm

1.200

1.325

Yes

14669 a

Exar SP485E

1.000

No

16 kohm b

0.750 b

1.750

Yes

  1. The RS-485 interface on the model 14669 is provided by the model 14673 plug-in option module.
  2. The 16 kohm network bias occurs with 14673 switches 1 and 2 in the OFF position, which is recommended. Placing these two switches in the ON position changes the bias to 8 kohm (1.5UL) and places a 120 ohm termination resistance across the network pair.

The provision of failsafe transceivers in the Legrand models 04677, 04680, and 04684 is a very beneficial feature. This type of transceiver with integrated failsafe receiver allows recommendation for a terminated bus without the negative limitation imposed with external bias resistors required to support termination. Configuration 1 supports these three meter models. For more information, see Legrand Configurations .

The model 14669 uses an older transceiver with no integrated failsafe feature and is rated for a full 1UL unit. This 1UL coupled with the internal bias resistance pushes the unit load of the model 14669 to a very high value of 1.75UL. This means each 14669 meter consumes almost two of the available 32 unit loads. Without the failsafe feature, the use of one of the alternate configuration options (2, 3, or 4) will be required. These configurations provide the required bias for the model 14669, but have the side effect of reduced node count and/or distance. For more information, see Legrand Configurations .

The models 04677, 04680, and 04684 can be used in any of the four configurations. If the network consists of only the models 04677, 04680, and/or 04684, Configuration 1 offers the best performance. If a single model 14669 is included on the network bus, the bus must use Configuration 2, 3, or 4 and follow the associated guidelines. For more information, see Legrand Configurations .

  • RS-485 Communications
  • Legrand Power Meters
  • Legrand Configurations