earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Specifications

Specifications


Products: IP-IO
Functionalities: Engineering, Hardware
Product version: 2022
12/17/2021

IP-IO

 
action_zoom_plus_stroke IP-IO module
Figure: IP-IO module

Introduction

SpaceLogic* IP-IO module provides I/O expansion to your HVAC application over BACnet/IP. The module can share its I/O resources across applications running in automation servers, BACnet/IP controllers, or third-party systems. With the support of local alarms and local trend logs, the IP-IO module avoids unnecessary traffic over the network while being able to log important information locally. The IP-IO module can be installed near facilities in the field, away from the automation server or the BACnet/IP controller. All IP-IO models support an optional display that provides insight and control of the inputs and outputs.

The IP-IO module has the following features:

  • IP enabled with dual-port Ethernet switch

  • Versatile onboard I/O point mix

  • Highly available

  • Commission mobile application for commissioning of the controller

  • Full EcoStruxure Building Operation software support, providing efficient engineering tools

For information on the maximum number of IP-IO modules that can be used with an automation server or a BACnet/IP controller, see the Architectural Guidelines.

* Formerly known as SmartX.

IP connectivity and flexible network topologies

The IP-IO module is based on open protocols that simplify interoperability, IP configuration, and device management:

  • IP addressing

  • BACnet/IP communications

  • DHCP for easy network configuration

The IP-IO module has a dual-port Ethernet switch, which enables flexible network topologies:

  • Star

  • Daisy chain

  • Rapid Spanning Tree Protocol (RSTP) ring

In a star topology, the IP-IO module and the parent EcoStruxure BMS server are individually connected to an Ethernet switch. Daisy-chain multiple IP-IO modules together to reduce the installation time and cost. Use an RSTP ring topology when you want a non-operational IP-IO module to be detected and recovered quickly and efficiently.

Models with a versatile mix of I/O points

The IP-IO module comes in three models with different I/O point count and a versatile mix of I/O point types that match a wide variety of applications. The universal inputs/outputs are highly flexible and can be configured as either inputs or outputs.

Table: I/O Point Types by IP-IO Models

I/O Point Types

IP-IO-DI10

IP-IO-UIO10

IP-IO-UIO5DOFA4

Digital inputs

10

-

-

Universal I/O

Type Ub

-

10

5

Relay outputs

Form A

-

-

3

High power relay outputs

Form A

-

-

1

Table: Configurations by I/O Point Types

Configurations

Digital Inputs

Universal I/O

Type Ub

Relay Outputs

Form A

High Power Relay Outputs

Form A

Digital inputs

yes

yes

-

-

Counter inputs

yes

yes

-

-

Supervised inputs

-

yes

-

-

Voltage inputs

(0 to 10 VDC)

-

yes

-

-

Current inputs

(0 to 20 mA)

-

yes

-

-

Temperature inputs

-

yes

-

-

Resistive inputs

-

yes

-

-

2-wire RTD temperature inputs

-

yes

-

-

Voltage outputs

(0 to 10 VDC)

-

yes

-

-

Digital outputs

-

-

yes

yes

Digital pulsed outputs

-

-

yes

yes

PWM outputs

-

-

yes

yes

Tristate outputs

-

-

yes

-

Tristate pulsed outputs

-

-

yes

-

Digital inputs

The digital inputs can be used for cost effective sensing of multiple dry contact digital inputs in applications, such as equipment status monitoring or alarm point monitoring. As counter inputs, digital inputs are commonly used in energy metering applications.

Universal inputs/outputs

The universal inputs/outputs are ideal for any mix of temperature, pressure, flow, status points, and similar point types in a building control system.

As counter inputs, the universal inputs/outputs are commonly used in energy metering applications. As RTD inputs, they are ideal for temperature points in a building control system. As supervised inputs, they are used for security applications where it is critical to know whether or not a wire has been cut or shorted. These events provide a separate indication of alarms and events in the system.

For all analog inputs, maximum and minimum levels can be defined to automatically detect over-range and under-range values.

The universal inputs/outputs can also be used as voltage outputs, without the need for external bias resistors. Therefore, the universal inputs/outputs support a wide range of devices, such as actuators.

Relay outputs

The relay outputs support digital Form A point types. The Form A relays are designed for direct load applications.

High power relay output

The high power relay output is ideal for switching loads of up to 12 A, such as electrical heating elements.

Highly available

The IP-IO module supports local trends and alarms, enabling local operation when the IP-IO module is offline.

With user-defined fallback values, the IP-IO outputs will be in a predictable state in cases of network disruption.

The battery-free power backup of the memory and real-time clock helps prevent data loss and allows seamless and quick recovery after a power disruption.

All IP-IO models can be equipped with a display add-on module (same module as used for the MP-C), which features an LCD display and five keys. With this module, you can manually override analog and digital outputs for testing, commissioning, and maintenance of equipment connected to the outputs. The display module's dedicated processing power ensures reliable override for maintenance applications. The override status can be viewed in EcoStruxure Building Operation WorkStation and WebStation, enabling precise monitoring and reliable control.

 
action_zoom_plus_stroke Display module
Figure: Display module

In WorkStation, you update the firmware of multiple IP-IO modules at the same time and with minimum down time. The EcoStruxure BMS server keeps track of the installed firmware to support backup, restore, and replacement of the IP-IO modules. The server can host IP-IO modules of different firmware versions.

Commission mobile application

The Commission mobile application is designed for local configuration, field deployment, and commissioning of IP-IO modules. The mobile application reduces the commissioning time, allows flexibility in project execution, and minimizes dependencies on network infrastructure.

The mobile application is designed for use with Android, Apple (iOS), and Microsoft Windows 10 devices. For more information, see the EcoStruxure Building Commission Specification Sheet.

 
action_zoom_plus_stroke Commission mobile application
Figure: Commission mobile application

Using the Commission mobile application, you can connect to IP-IO modules and BACnet/IP controllers over the network. Using a wireless access point or a network switch, you can connect to a network of IP-IO modules and BACnet/IP controllers on the local IP network.

Device configuration

With the Commission mobile application, you can easily discover IP-IO modules and BACnet/IP controllers on the IP network. You can change the configuration of each module and controller, including the BACnet and IP network settings, location, and parent server. To save engineering time, you can save common device settings and then reuse them for devices of the same type and model.

Field deployment and I/O checkout

The Commission mobile application does not require an EcoStruxure BMS server or a network infrastructure to be in place. You can use the mobile application to load the IP-IO application directly into the local IP-IO module and deploy the IP-IO module. The IP-IO application can be created offline using Project Configuration Tool or WorkStation while preserving all external bindings to server and controller applications using the IP-IO module's I/O points. You can also perform an I/O checkout to ensure that the IP-IO module's I/O points are configured, wired, and operating correctly.

Full EcoStruxure Building Operation software support

The power of the IP-IO module is fully realized when it is part of an EcoStruxure BMS, which provides the following benefits:

  • WorkStation/WebStation interface

  • Device discovery

  • Engineering efficiency

WorkStation/WebStation interface

WorkStation and WebStation provide a consistent user experience regardless of which EcoStruxure BMS server the user is logged on to. The user can log on to the parent EcoStruxure BMS server to engineer, commission, supervise, and monitor IP-IO modules and BACnet/IP controllers. For more information, see the WorkStation and WebStation specification sheets.

Device discovery

The enhanced Device Discovery in WorkStation enables you to easily identify IP-IO modules on a BACnet network and to associate the IP-IO modules with their parent server.

Engineering efficiency

The engineering and maintenance of IP-IO modules can be done very efficiently using the EcoStruxure Building Operation reusability features. With these features, you can create library items (Custom Types) for a complete IP-IO application that contains I/O point configurations and all necessary objects such as trends and alarms. The IP-IO application in the Custom Types library is reusable across all IP-IO modules of the same model. You can use the IP-IO application as a base for creating new IP-IO modules intended for similar applications. You can then edit the IP-IO application, and the changes are automatically replicated to all IP-IO modules, while each IP-IO module keeps its local values.

WorkStation supports both online and offline engineering of IP-IO modules. You can make the configuration changes online or use database mode to make the changes offline. In database mode, the changes are saved to the EcoStruxure Building Operation database so that you can apply the changes to the IP-IO modules later.

Project Configuration Tool enables you to perform all the engineering off site, without the need for physical hardware, which minimizes the time you need to spend on site. You can run the EcoStruxure BMS servers virtually and engineer the BACnet/IP controllers and IP-IO modules before you deploy your server, controller, and IP-IO applications to the servers, controllers, and IP-IO modules on site. For more information, see the Project Configuration Tool specification sheet.

In addition, you can use Automated Engineering Tool to facilitate your engineering process when using IP-IO modules. This tool provides access to a library of standard IP-IO applications that can be quickly configured and customized using the wizards and mass edit functions provided in the tool. You can then load these customized applications into your target server. The tool also enables the quick creation of your own templates based on IP-IO applications that you have developed. These templates facilitate a standard approach and easy reuse and duplication of common IP-IO applications. For more information, see the Automated Engineering Tool specification sheet.

 
action_zoom_plus_stroke Library of standard HVAC applications
Figure: Library of standard HVAC applications

Table: Part Numbers

Product

Part number

IP-IO-DI10
SXWIPIOAA10001
IP-IO-UIO10
SXWIPIOBA10001
IP-IO-UIO5DOFA4
SXWIPIOCA10001
MP-C DISPLAY
(MP-C override display module)
SXWMPCDSP10001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001

For more information on part numbers for Network Connectivity Accessories, see the For more information, see Product Selection Guide - EcoStruxure Building ..

Specifications

AC input
Nominal voltage
24 VAC
Operating voltage range
+/- 20 %
Frequency
50/60 Hz
Maximum power consumption
17 VA
Power input protection
MOV suppression and internal fuse
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption
9 W
Power input protection
MOV suppression and internal fuse
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation a
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only a
a) MP-C Display has an operating temperature range of -30 to +60 °C (-22 to +140 °F).
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5V
Ingress protection rating
IP 20
Mechanical
Dimensions
153 W x 110 H x 64 D mm (6.0 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, IP-IO-DI10
Including terminal blocks
0.337 kg (0.742 lb)
Weight, IP-IO-UIO10
Including terminal blocks
0.336 kg (0.740 lb)
Weight, IP-IO-UIO5DOFA4
Including terminal blocks
0.357 kg (0.787 lb)
Installation
DIN rail or other flat surface inside a cabinet
Terminal blocks
Removable
Software compatibility
EcoStruxure Building Operation software
version 2.0 or later
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN 50491-5-2; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2; BS/EN 50491-5-3
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN 50491-3; UL 916 C-UL US Listed
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BTL B-ASC (BACnet Application Specific Controller) a
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page.
CPU
Frequency
500 MHz
Type
ARM Cortex-A7 dual-core
DDR3 SDRAM
128 MB
NOR flash memory
32 MB
Memory backup
128 kB, FRAM, non-volatile
MP-C Display (Optional)
Removable
No
Display size
36 W x 17 H mm (1.4 W x 0.7 H in.)
Display resolution
128 x 64 pixels
Display type
FSTN monochrome LCD, white color transflective backlight
Power consumption
max. 0.15 W (45 mA at 3.3 V)
Ambient temperature, operating
-30 to +60 °C (-22 to +140 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Weight
0.035 kg (0.077 lb)
Compliance with standards
EN ISO 16484-2
Digital inputs, DI
Channels, IP-IO-DI10
10, DI1 to DI10
Channels, IP-IO-UIO10
0
Channels, IP-IO-UIO5DOFA4
0
Absolute maximum ratings
-0.5 to +24 VDC
Digital input protection
Transient voltage suppressor on each digital input
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
150 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
Universal inputs/outputs, Ub
Channels, IP-IO-DI10
0
Channels, IP-IO-UIO10
10 Ub, Ub1 to Ub10
Channels, IP-IO-UIO5DOFA4
5 Ub, Ub1 to Ub5
Absolute maximum ratings
-0.5 to +24 VDC
A/D converter resolution
16 bits
Universal input/output protection
Transient voltage suppressor on each universal input/output
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
150 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
Supervised inputs
5 V circuit, 1 or 2 resistors
Monitored switch combinations
Series only, parallel only, and series and parallel
Resistor range
1 to 10 kohm
For a 2-resistor configuration, each resistor must have the same value +/- 5 %
Voltage inputs
Range
0 to 10 VDC
Accuracy
+/-(7 mV + 0.2 % of reading)
Resolution
1.0 mV
Impedance
100 kohm
Current inputs
Range
0 to 20 mA
Accuracy
+/-(0.01 mA + 0.4 % of reading)
Resolution
1 μA
Impedance
47 ohm
Resistive inputs
10 ohm to 10 kohm accuracy
+/-(7 + 4 x 10 -3 x R) ohm
R = Resistance in ohm
10 kohm to 60 kohm accuracy
+/-(4 x 10 -3 x R + 7 x 10 -8 x R 2 ) ohm
R = Resistance in ohm
Temperature inputs (thermistors)
Range
-50 to +150 °C (-58 to +302 °F)
Supported thermistors
Honeywell
20 kohm
Type I (Continuum)
10 kohm
Type II (I/NET)
10 kohm
Type III (Satchwell)
10 kohm
Type IV (FD)
10 kohm
Type V (FD w/ 11k shunt)
Linearized 10 kohm
Satchwell D?T
Linearized 10 kohm
Johnson Controls
2.2 kohm
Xenta
1.8 kohm
Balco
1 kohm
Measurement accuracy
20 kohm
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
  
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
10 kohm, 2.2 kohm, and 1.8 kohm
-50 to -30 °C: +/-0.75 °C (-58 to -22 °F: +/-1.35 °F)
  
-30 to +100 °C: +/-0.2 °C (-22 to +212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
Linearized 10 kohm
-50 to -30 °C: +/-2.0 °C (-58 to -22 °F: +/-3.6 °F)
  
-30 to 0 °C: +/-0.75 °C (-22 to +32 °F: +/-1.35 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
1 kohm
-50 to +150 °C: +/-1.0 °C (-58 to +302° F: +/-1.8 °F)
RTD temperature inputs
Supported RTDs
Pt1000, Ni1000, and LG-Ni1000
Pt1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +70 °C (-58 to +158 °F)

+/-0.5 °C (+/-0.9 °F)

0 to 50 °C (32 to 122 °F)

70 to 150 °C (158 to 302 °F)

+/-0.7 °C (+/-1.3 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-1.0 °C (+/-1.8 °F)

Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

LG-Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

RTD temperature wiring
Maximum wire resistance
20 ohm/wire (40 ohm total)
Maximum wire capacitance
60 nF
The wire resistance and capacitance typically corresponds to a 200 m wire.
Voltage outputs
Range
0 to 10 VDC
Accuracy
+/-60 mV
Resolution
10 mV
Minimum load resistance
5 kohm
Load range
-1 to +2 mA
Relay outputs, DO
Channels, IP-IO-DI10
0
Channels, IP-IO-UIO10
0
Channels, IP-IO-UIO5DOFA4
3, DO1 to DO3
Contact rating
250 VAC/30 VDC, 2 A, Pilot Duty (C300)
Switch type
Form A Relay
  
Single Pole Single Throw
  
Normally Open
Isolation contact to system ground
3000 VAC
Cycle life (Resistive load)
At least 100,000 cycles
Minimum pulse width
100 ms
High power relay outputs, DO
Channels, IP-IO-DI10
0
Channels, IP-IO-UIO10
0
Channels, IP-IO-UIO5DOFA4
1, DO4
Contact rating
250 VAC/24 VDC, 12 A, Pilot Duty (B300)
Switch type
Form A Relay
  
Single Pole Single Throw
  
Normally Open
Isolation contact to system ground
5000 VAC
Cycle life (Resistive load)
At least 100,000 cycles
Minimum pulse width
100 ms

Terminals

Follow proper installation wiring diagrams and instructions, including these instructions:

  • All IP-IO models have several RET terminals for connection of I/O returns, so a common chassis/signal ground rail is optional and may not be needed.

  • Individual 24 V power sources to the field must be current limited to maximum 4 A for UL compliant installations, and maximum 6 A in other areas.

  • For more information on wiring, see Hardware Reference Guide.

 
action_zoom_plus_stroke IP-IO-DI10
Figure: IP-IO-DI10
 
action_zoom_plus_stroke IP-IO-UIO10
Figure: IP-IO-UIO10
 
action_zoom_plus_stroke IP-IO-UIO5DOFA4
Figure: IP-IO-UIO5DOFA4
  • Enterprise Server
  • AS-P
  • AS-B
  • WorkStation
  • WebStation
  • MP-C
  • MP-V
  • Commission
  • Project Configuration Tool
  • Automated Engineering Tool
  • Architectural Guidelines 4.0.1, 4.0.2, and 4.0.3